The 50 amp service is two legs of 110v, and they are out of phase so you do have 220 between them like a regular 220v circuit does. But your MH does not use 220v anywhere, it is always just one leg. Not that you are stuck with that, but if you ever are in a 30 amp plug, then you only have 110v. So you will not be able to use the dryer.
Your generator likely does have 220v, it is just not wired in your MH to take advantage of it.