FYI - Not sure if you are worried about complying with any codes, but National Electrical Code (NEC) does not allow an electrical panel to be installed with a bathroom. The code sections would be 230-70(a) and 240-24(e) This is mainly because the panel would be to close in proximity to wet locations. (This applies even if you use a weather proof panel). any electrical outlets need to be GFCI protected if within 6' of a water source also.