View Single Post
Old 05-15-2012, 12:16 PM   #3
mmmc101
Senior Member
 
mmmc101's Avatar
 
Join Date: Feb 2009
Location: Choctaw,Okla
Posts: 174
Default

Dick, I would pour it 5 inches if you plan on a 379 Pete. The truck will have 10-12K on the steering axle and that is on a small footprint. I also would use 1/2 inch rebar on 2ft centers with 3500 psi concrete. I have built 6 commercial steel buildings in the last two years and have not had any problems with the driveways or floors. Most were for commercial trucks or large motorhomes. My cost for material (3500 psi concrete, steel,sand) runs about $2.50 per square foot for a 5 inch floor/driveway. Anything above that is labor.
Attached Thumbnails
052.jpg   barn 006.jpg   barn 013.jpg   barn 010.jpg  
mmmc101 is offline   Reply With Quote